Brass bus bar
Goto page 1, 2  Next
fvalarm(at)rapidnet.net
PostPosted: Wed Jun 01, 2011 9:50 pm    Post subject: Brass bus bar Reply with quote
Can you tell me how much current the 1/2" wide (.025 thick) brass bus bar
stock that B&C sells can comfortably handle? It would be a short piece,
about 3 inches long if that makes a difference?
Bevan
RV7A
PostPosted: Thu Jun 02, 2011 10:30 am    Post subject: Brass bus bar Reply with quote
At 01:47 AM 6/2/2011, you wrote:
--> AeroElectric-List message posted by: "B Tomm" <fvalarm(at)rapidnet.net>
It will carry a LOT of current but it does
have a significant temperature rise if subjected
to starter currents.
.025 is a bit skinny. I think all the brass
(and copper) straps I've seen on airplanes is
at least .050 if not thicker. See:
http://aeroelectric.com/Pictures/Wiring_Technique/Contactor_Interconnect/
Brass has a small fraction the electrical conductivity
of copper. Look for a display like this:
[img]cid:.0[/img]
In your hardware store or hobby shop. I think it includes
copper sheets in .025 which would be much better and
probably adequate.
Also consider soldering up a short piece of welding
cable with terminals of appropriate spacing.
http://www.aeroelectric.com/articles/big_term.pdf
Brass isn't out of the question . . . but it's
not the best choice.
 Filesize:  94.69 KB
 Viewed:  22013 Time(s)
dougshep
PostPosted: Sat Jun 04, 2011 3:30 pm    Post subject: Brass bus bar Reply with quote
If soldering is not necessary, Could a strip of Aluminum be used for the bus bar?
Doug Shepard, RV-9A
PostPosted: Sat Jun 04, 2011 6:06 pm    Post subject: Brass bus bar Reply with quote
Thanks Bob,
I found a strip of stainless. .028 thick X 3/4 wide. I believe the
terminals of the BlueSea ANL holders are stainless. I applied some terminal
conductive paste for corrosion control on the aluminum ring terminals. The
Stainless strip connects the two ANL holders. We'll see how this combo
holds up. All parts are easily accessible and replaceable if necessary
after flying. Thanks for the responses.
Bevan
PostPosted: Sun Jun 05, 2011 8:02 am    Post subject: Brass bus bar Reply with quote
At 10:02 PM 6/4/2011, you wrote:
Thanks Bob,
Hmmmm . . .
Keep in mind that the threaded fasteners used to
hold things together are just that . . . designed
to hold things together. In this case we're hoping
to put sufficient 'mash' on OTHER materials that
are the current carrying conductors such that large
areas of 'gas tightness' are achieved. Those are typically
tin-plated copper terminals.
Folks who float boats have an environmental
stress not common to airplanes. Corrosion.
There's a strong reason to look for more
materials more robust in the salt-air.
But that's a trade off. Stainless is, I
believe, less conductive than brass. So
heating of the material may well contribute
to joint failure. Stainless is harder too,
the area of "gas-tightness" is lower for
the same-mate up forces. Aluminum gets you
some pretty good contact area but it is the
most reactive of the metals we've discussed.
Thick brass or thinner copper are the
materials of choice for jumpers between
fat-terminals. ESPECIALLY if those jumpers
carry starter currents. Stainless and
particularly aluminum are not recommended.
Stainless HARDWARE to hold things together
is fine . . . where conductors come together
with other conductors is our focus for
performance.
Bob McC
PostPosted: Sun Jun 05, 2011 10:08 am    Post subject: Brass bus bar Reply with quote
Without going into detail of units etc, the relative resistivity of common
conductors is as follows. The best common conductor is silver, with copper a
close second. Stainless is waaay down the list. A smaller number represents
a better conductor from a purely conductive viewpoint. (The smaller the
number the less losses) Best to stick to copper conductors wherever feasible
with the possible exception of Eric's copper clad aluminium for very long
heavy runs. ( http://www.periheliondesign.com/fatwires.htm )
Silver 15.9
Copper 17.1
Aluminium 26.5
Brass 64.0
Mild steel 180
Stainless steel 720
Nichrome 1500 (used for heating elements)
Bob McC
[quote] --
Bob McC
Falco #908
(just starting)
henador_titzoff(at)yahoo.
PostPosted: Sun Jun 05, 2011 12:55 pm    Post subject: Brass bus bar Reply with quote
I'm not sure where you got those "relative resistivity" numbers below, as I've always seen metals and other substances' resistance described as Ohms/meter. However, I checked the resistance of silver over copper and compared them to your numbers below (15.9/17.1), and the ratios are the same.
I just want to point out that gold should be in there between copper and aluminum. Gold is widely used in the electronics industry to plate connector pins and sockets, on integrated circuits to connect die to pins and pads, and on circuit board pads. No doubt there are countless other uses for gold in electrical circuits.
Eric's fat wires are a great trade off between resistivity, weight and volume. It's one of the best simple ideas to come out of the aerospace industry. My hat off to Eric for being one of our vendors!
Henador Titzoff
From: Bob McCallum <robert.mccallum2(at)sympatico.ca>
Sent: Sunday, June 5, 2011 2:04 PM
Subject: RE: Brass bus bar
--> AeroElectric-List message posted by: Bob McCallum <robert.mccallum2(at)sympatico.ca (robert.mccallum2(at)sympatico.ca)>
Silver   15.9
Copper   17.1
Aluminium 26.5
Brass  64.0
Mild steel 180
Stainless steel 720
Bob McC
[quote] --
PostPosted: Sun Jun 05, 2011 4:41 pm    Post subject: Brass bus bar Reply with quote
At 04:52 PM 6/5/2011, you wrote:
There's a fist full of ways to describe the relative
resistance of materials. Obviously, it's a volume thing.
A bar of copper 1" square and 10' long will show a much
lower resistance than a .1" square that is also 10' long.
Any chart that speaks to relative resistivity of materials
will be incomplete without building definitions around
the samples for which the numbers are cited. For example.
Here's a chart I found on the 'net . . .
http://tinyurl.com/3w4m4kp
[img]cid:.0[/img]
Some resistivity charts have been published using copper
as a baseline and assigning it the value 1.0 with all other
metals compared to copper. Similar charts have been made
with silver having the base-line assignment of 1.0. MOST
such charts are used to calculate the ratio of RELATIVE
resistance between two different materials.
The chart above does us the service of adding a cross-section
that's well known, like 10AWG wire. Note the similarity
of this value to the resistance for copper wire published in
the 'Connection. VERY close to 1 millohm/foot.
RESISTANCE is always a point-to-point measurement like
from one end of a resistor to the other, two different
points in a circuit, one end of a wire to another. The
value observed may be the sum effects of many resistances.
RESISTIVITY always speaks to the volumetric resistance
of a homogenous but otherwise single material . . . like
a bar of brass, copper or stainless steel.
Yes! Thanks for mentioning it. The primary use for gold
is corrosion protection. It's not a terribly good
conductor but it is very resistant to corrosion. This
explains the popularity for putting the very smallest
layers of gold on a connector's mating surfaces. Typically
50 micro-inches or less.
 Filesize:  113.74 KB
 Viewed:  21973 Time(s)
rparigoris
PostPosted: Sun Jun 05, 2011 5:40 pm    Post subject: Re: Brass bus bar Reply with quote
Hi Bob
A while back I put together a list of links for galvonic and conductivity info:
http://www.europaowners.org/forums/gallery2.php?g2_itemId=87240
It's in word format, you need to click on "download document".
Ron Parigoris
mrspudandcompany(at)veriz
PostPosted: Mon Jun 06, 2011 4:17 am    Post subject: Brass bus bar Reply with quote
So, me thinks that the best conclusion from this thread is:  If you want the best bus, use a gold plated silver bar.  This will give you the lowest resistance and the highest rejection of corrosion.  Mine will be on order as soon as my house refinancing goes through ☺☺☺
            Roger
bbradburry(at)bellsouth.n
Henador would know about gold. He used solid gold in all his fat wires. When the engine fails to catch, he just flies on the starter! :>)
B2
From: owner-aeroelectric-list-server(at)matronics.com [mailto:owner-aeroelectric-list-server(at)matronics.com] On Behalf Of Henador Titzoff
Sent: Sunday, June 05, 2011 4:53 PM
Subject: Re: AeroElectric-List: Brass bus bar
Henador Titzoff
Subject: RE: AeroElectric-List: Brass bus bar
Silver 15.9
Copper 17.1
Aluminium 26.5
Brass 64.0
Mild steel 180
Stainless steel 720
Bob McC
PostPosted: Mon Jun 06, 2011 6:29 am    Post subject: Brass bus bar Reply with quote
Save your house and go with copper plated aluminum or just copper. I'll even finance it for you. Smile
Henador Titzoff
From: ROGER & JEAN CURTIS <mrspudandcompany(at)verizon.net>
Sent: Monday, June 6, 2011 8:13 AM
Subject: AeroElectric-List: Brass bus bar
Roger
PostPosted: Mon Jun 06, 2011 7:17 am    Post subject: Brass bus bar Reply with quote
Thank you very much, Ron. I checked out your website and found one link to a "relative resistivity" chart that I really like. It's really a relative conductivity chart, which is of course the reciprocal. It shows copper to be 100%, and it compares everything to it. Silver, for example, has a conductivity of 105%.
I really like this chart and info below it. It says that although brass has a large percentage of copper, its conductivity is degraded much more by the additive metals than the percentages of them in brass. I never use brass for electrical conduction, although it can be used for RFI shielding.
Henador Titzoff
Sent: Sunday, June 5, 2011 9:40 PM
Subject: AeroElectric-List: Re: Brass bus bar
--> AeroElectric-List message posted by: "rparigoris" <rparigor(at)suffolk.lib.ny.us (rparigor(at)suffolk.lib.ny.us)>
Hi Bob
Ron Parigoris
http://forums.matronics.com/viewtopic.php?p=34215========================
PostPosted: Mon Jun 06, 2011 7:18 am    Post subject: Brass bus bar Reply with quote
Seriously, what I used, and find that it works great and is
inexpensive is, 3/8" soft copper tubing. Take the tubing and flatten it in
your vice and it becomes a nice bar that you can solder on tabs, and it will
carry the current load.
Roger
winmail.dat
 Filename:  winmail.dat
 Filesize:  4.54 KB
 Downloaded:  965 Time(s)
rparigoris
PostPosted: Mon Jun 06, 2011 10:14 am    Post subject: Re: Brass bus bar Reply with quote
Hi Henador
"Thank you very much, Ron. I checked out your website and found one link to a "relative resistivity" chart that I really like. It's really a relative conductivity chart, which is of course the reciprocal. It shows copper to be 100%, and it compares everything to it. Silver, for example, has a conductivity of 105%."
I too like that chart.
I have been using copper bus bars (and thin wires):
http://www.europaowners.org/forums/gallery2.php?g2_itemId=30710
and silver plating using cool amp:
http://www.cool-amp.com/
When copper oxidizess it doesn't conduct very well, silver when it tarnishes it still conducts somewhat. I find it easy to use, it is non toxic and if I let plain copper sit around it needs cleaning before use which sometimes is a pain, but the plated parts are still beautiful.
I did a test leaving some plain copper bus and some plated copper bus sit in my yard for some time (probably more than a year). The copper is dark brown and will not solder at all unless cleaned. the silver plated bus is a little tarnished but still solders OK believe it or not.
I should take a pic of what this thin wide wire/bus looks like now:
http://www.europaowners.org/forums/gallery2.php?g2_itemId=30937
I plated the end in the foreground with six screws, I also plated just a hole punch sized spot. Now the copper is plenty brown just sitting around in the hangar. the silver plate still looks great. Now the other end is plated, but if you had to clean oxidized copper there for final assembly like I did a few months ago, what a pain.
Ron Parigoris
PostPosted: Mon Jun 06, 2011 11:20 am    Post subject: Brass bus bar Reply with quote
Groan, Ron! The prices of the Cool-Amp is $231.87 for a 16 oz bottle and Conducto-Lube is $496.72 for a 8 oz bottle! At those prices, I'd have to sell my house and outsource my wife! I like much better burnishing the corrosion off the copper, which is easy to do and cheap. This business of using silver bus bar or Cool-Amp/Conducto-Lube is okay for the US government, which we all know has an endless bucket of money. Smile
I could see using these two materials in our experimental airplanes if there was a reliability problem that we're trying to solve; however, I haven't heard of one, and a one foot of 1/8"x1/2" C110 H04 copper bus bar costs only $3.16 at OnlineMetals.com, plus shipping. I think this is reasonable.
Henador Titzoff
Sent: Monday, June 6, 2011 2:14 PM
Subject: Re: Brass bus bar
Hi Henador
Ron Parigoris
http://forums.matronics.com/viewtopic.php?p=342214#342214
PostPosted: Mon Jun 06, 2011 2:13 pm    Post subject: Brass bus bar Reply with quote
Such potions are mostly intended for connectors that
can be mated/de-mated with some frequency and do not
enjoy gas-tight make-up of the contacts.
The only time you might get some benefit for permanent
joints is if they've been made up too loose to begin
with. Those products are popular with the maintenance
folks in factories, etc. but I've never seen them
called out on an airplane drawing anywhere.
Bob . . . [quote][b]
rparigoris
PostPosted: Mon Jun 06, 2011 2:13 pm    Post subject: Re: Brass bus bar Reply with quote
Hi Henador
If you take a look on cool Amps site they sell a 2 oz. jar for $43.95
If you go in with some of your buddies (probably up to 10) you all will have a lifetime supply.
A sixteen oz. jar would be good for probably a lifetime supply for 80 builders.
There are problems with copper. There are places where if it oxidizes it is hard to clean. For instance my port and starboard connecting copper thin wide wire. They plate copper lugs for that same reason, would be hard to clean internal portion.
Cool amp also works on brass. My Flaming River race car cut off contactor got the threads and mounting hardware plated as well. Again it was installed a while ago and hard to remove to clean contact areas. the silver plating a few months ago were in very nice condition where other brass stuff would in fact need burnishing.
Ron Parigoris
PostPosted: Mon Jun 06, 2011 3:47 pm    Post subject: Brass bus bar Reply with quote
Ron,
Usually going in with the guys doesn't work, as one of them will use Cool-Amps to do his whole house and poof, it's gone! Either that or nobody knows where it is anymore.  I've found that as you involve 2 or more people in any effort, it gets complicated.
Great product, but the real reason that Cool-Amps is not cost effective for what we're doing is because it is a solution (no pun intended) looking for a problem. AE bus bar designs are so easy to get to on our airplanes that even Kim Kardashian could burnish one for you. As Bob pointed out, gas tight fittings have been solving the corrosion problem for decades.
Henador Titzoff
Sent: Monday, June 6, 2011 6:13 PM
Hi Henador
Ron Parigoris
http://forums.matronics.com/viewtopic.php?p=342250#342250< --> &nbsp========================
Eric M. Jones
PostPosted: Tue Jun 07, 2011 7:12 am    Post subject: Re: Brass bus bar Reply with quote
By the way. My local airport, Southbridge, MA had 33 aircraft of which 30 were totalled by a tornado last week. Jeeeeezz..........
On the subject of wires and materials, as has been mentioned. Silver is the best conductor ---and this is the important part--per unit volume. Aluminum is 2X as good as anything else in the universe per unit mass. This is important to people where weight (and MONEY) is concerned.
I sell a lot of Copper-Clad Aluminum to race car drivers, helicopter builders and anyone who wants to lose a pound or two. I sell many thousands of feet to military drone builders. I even sell to top-fuel dragsters. (Hey, I can shave a pound off your 320 mph in 1/4 mile dragster!).
But for really short runs, or bus bars, it doesn't save much. There is a copper clad aluminum bus bar material (which I am considering carrying), but I really recommend configuring wiring so as to not need a bus bar.
Factoid: Gold is good for low corrosion and its resulting low resistance. But it only makes sense for very low voltages/currents. You might think gold might would be a great conductor, but it isn't.
Factoid: Stainless Steel and Aluminum are problematic when oxidized. Copper and a few other metals work even if oxidized, but curiously CuO etc. was used for diodes. This can cause bizarre electrical problems--for example at high frequencies, strange DC biases appear. This is a problem in electro-surgery where the connection may have been electroplated but now the plating has scratches, chips and corrosion. I surmise that transmitters are not totally immune to this, so keep those connections clean and tight.
Eric M. Jones
www.PerihelionDesign.com
113 Brentwood Drive
Southbridge, MA 01550
(508) 764-2072
emjones(at)charter.net
Goto page 1, 2  Next