Z-14 Question
bushpilot(at)optonline.ne
PostPosted: Sat Feb 11, 2006 9:21 am    Post subject: Z-14 Question Reply with quote
Bob,
The primary small gage wiring on the design is 4 AWG. Between the cross feed contactor and the main battery contactor you show a 2 AWG. This is the only place on the design that is using a 2 AWG wire. Why does it need to be 2 AWG? Will 4 AWG work?
Johnathan
nuckollsr(at)cox.net
PostPosted: Thu Feb 23, 2006 9:21 am    Post subject: Z-14 Question Reply with quote
At 12:17 PM 2/11/2006 -0500, you wrote:
<bushpilot(at)optonline.net>
Bob,
Johnathan
Keep in mind these are architecture drawings. Details as to
wire sizing, fuse/breaker sizing, etc are variables that need
attention during the design of YOUR system. The Z-figures
are not all combed for agreement of the variables. If 4AWG
was adequate for the fat wires in the rest of your system, then
2AWG is not necessary to jumper contactors.
< with experiment. >
< --Lawrence M. Krauss >